shore power inlet front of 5ver, EMS protection


lockmup68

Recommended Posts

2007 Teton, has gen prep package (automatic transfer switch and wiring to the location of where gen set is mounted).

Just wanted to make sure I'm not under thinking this, I have the gen prep package, ATS is already installed, the wiring is in a junction box near the front of the basement. To add a front shore power plug, I think I simply wire in new shore power plug to the existing wires in the gen prep junction box. What am I missing? 

2nd question, I have a progressive industries hardwire EMS. I assume this should be wired in AFTER the automatic transfer switch, that way either power input source (front or back input) will be protected. 

I want a front plug for several reasons, namely, the genset is on the truck vs. mounted on the trailer, and secondly, many power pedestals are now closer to the front of the trailer vs. the rear where you want to park in the spot. I hate pulling the 50 amp extension cord as it seems I am frequently just 3 feet short in cord length. 

Thanks,

2003 International Eagle 9200i, Cummins ISX, Freedomline

2007 Teton Scottsdale XT4

 

Link to comment
Share on other sites

From my understanding of what you are trying to do, others have done something similar. Jack Mayer has a two shore power sources (front, back) going to a transfer switch and then through the Progressive Industries EMS (EMS-HW50C). I'm sure he will comment.

I'm looking at a new coach design and would do something similar. My only concern is having the TS (PD52) as a Single Point of Failure (SPOF) before the EMS systems. Could use two EMS systems, one of each source line, before the transfer switch. That would provide EMS protection, power usage monitoring to both lines, but more expensive. So curious on what other power distribution approaches people suggest (Jack, oldjohnt, etc.)

Link to comment
Share on other sites

1 hour ago, lockmup68 said:

To add a front shore power plug, I think I simply wire in new shore power plug to the existing wires in the gen prep junction box. What am I missing? 

The only negative that I can think of for this approach would be that when you use power from the secondary source to the ATS it means that the coil of the ATS is energized for as long as you are using that power source. For most users that is of little consequence because a generator is not typically used constantly for months at a time, while the shore power cord might be. The effect could mean a somewhat shorter lifespan for the ATS but I have never seen any data on that so I doubt that it would be very significant, but might be something to consider. 

1 hour ago, lockmup68 said:

2nd question, I have a progressive industries hardwire EMS. I assume this should be wired in AFTER the automatic transfer switch, that way either power input source (front or back input) will be protected. 

2

That is correct in order to be protected when using the front cord. While most generators are supposed to not need such protection,  I'm not sure that I entirely believe that and I know that I would want it in the circuit when using the front cord to connect to a shore power pedestal. 

Good travelin !...............Kirk

Full-time 11+ years...... Now seasonal travelers.
Kirk & Pam's Great RV Adventure

            images?q=tbn:ANd9GcQqFswi_bvvojaMvanTWAI

 

Link to comment
Share on other sites

Both shore powers to an ATS, rear shore primary. Then output from ATS to Progressive, then from progressive to loadcenter. No issues with that at all....it is done all the time.

 

Jack & Danielle Mayer #60376 Lifetime Member
Living on the road since 2000

PLEASE no PM's. Email me. jackdanmayer AT gmail
2016 DRV Houston 44' 5er (we still have it)
2022 New Horizons 43' 5er
2016 Itasca 27N 28' motorhome 
2019 Volvo 860, D13 455/1850, 236" wb, I-Shift, battery-based APU
No truck at the moment - we use one of our demo units
2016 smart Passion, piggyback on the truck
-------------------------------------------------------------------------
See our website for info on New Horizons 5th wheels, HDTs as tow vehicles, communications on the road, and use of solar power
www.jackdanmayer.com
Principal in RVH Lifestyles. RVH-Lifestyles.com

Link to comment
Share on other sites

I have a 50 amp plug in the front as well as the gen set on one transfer switch. The plug is primary and the gen set is secondary on that switch. This is then run to the rear of the coach as a secondary input on the main transfer switch. The rear 50 amp connection is the primary on that transfer switch. From there it goes to the Progressive Industries surge and then to the load center. That way I can have front or rear hookups or run the gen set without changing anything.

2023 Thor Magnitude XG32

Link to comment
Share on other sites

If I'm correctly understanding what you're doing, it works for me as the fine gents above, and I'm over safety conscious remember.

As you use shower power much more then the Genset, I see that obviously as PRIMARY input to the ATS with the Genset as Secondary (covers Kirks valid concern) and ATS output to the EMS (so genny or utility is protected) then to your distribution panel.

Is the ATS a two or a three pole?? IE does it switch Neutral as well as the two hots ?? I'm assuming the Genset, as most larger units, has a bonded Neutral.  

John T 

Link to comment
Share on other sites

ATS switches three wires.  Many ATS relays are powered to make contact, a relay for each source.  Very few are double pole where  off is shore and on is generator.

We had two input connectors with a ATS between them.  The output went to the ATS for the generator.  Our EMS plugged into the power pole.

We used an ATS between the two input connectors so that when one was in use, the other was dead to prying kiddy fingers.

Please click for Emails instead of PM
Mark & Dale
Joey - 2016 Bounder 33C Tige - 2006 40' Travel Supreme
Sparky III - 2021 Mustang Mach-e, off the the Road since 2019
Useful HDT Truck, Trailer, and Full-timing Info at
www.dmbruss.com

Link to comment
Share on other sites

1 hour ago, Mark and Dale Bruss said:

ATS switches three wires

Mark, that would be my expectation as necessary to switch two hots and the Neutral on a 50 amp 120/240 system. That way single point grounding is maintained and the Genset has the typical for larger units bonded Neutral, works for me. Its possible to switch only the Hots but that's another story. Indeed if two shore power connections are tied together you need it configured so no live pins might be exposed YIKES

John T  

Link to comment
Share on other sites

If the EMS is before the TS won't it protect the circuit board in the transfer switch.

Some TS use terminal strips to connect 6ga wire. On the other side of terminal strip fom the 6ga there are 2-10ga wires. If the load is not balanced the neutral may carry more than the 10ga is capable of.

2011 Cameo 34SB3

Link to comment
Share on other sites