Two Air Conditioners 8KW Generator


Kevor

Recommended Posts

Looking at a 2013 Tiffen Phaeton 40QBH. This model has the standard two air conditioners with an 8KW generator. I was looking for the upgrade with 3 AC units and 10KW generator. Can anyone share pros/cons of the 2 AC units/8KW generator?

Thanks

Link to comment
Share on other sites

We have a 2004 Newmar Dutch Star w/(2) Dometic 13.5 BTU AC/Heatpumps and a 7.5 Cummins-Onan diesel genie. Have not had "any" issues running both airs simultaneously, along with the convection/microwave oven; etc. We set the stat at 72, occasionally change from auto fan speed to low or high and have never had any cooling issues or lack of gennie capacity. The present setup of what your looking at will be fine; (unless you have money to burn and want the additional stuff) :D

Link to comment
Share on other sites

We have a 2004 Newmar Dutch Star w/(2) Dometic 13.5 BTU AC/Heatpumps and a 7.5 Cummins-Onan diesel genie. Have not had "any" issues running both airs simultaneously, along with the convection/microwave oven; etc. We set the stat at 72, occasionally change from auto fan speed to low or high and have never had any cooling issues or lack of gennie capacity. The present setup of what your looking at will be fine; (unless you have money to burn and want the additional stuff) :D

Nope, no money to burn. Thanks very much for your reply.

Link to comment
Share on other sites

Where do you plan to travel? If you are sticking to the northern half of the US, you will be fine. If you are planning on touring the SW in the summer, then 2 A/C units might leave you feeling a bit warm. I have a 36' Phaeton with the 8K generator and we are fine here in the SW. But if I had a 40', I would want an additional A/C unit.

Link to comment
Share on other sites

 

Your 8KW probably could handle 3 AC depending on the size/make of them.

 

I'd be very leery of trying that. I have had experience with a MH (not mine) on which a third A/C was added to a rig with an 8kW generator. It didn't have a load management system and, as a result, there was no way to avoid having the starting surges periodically occur at the same time. The owner experienced several A/C failures before it was realized that the source of the problem was the extra A/C.

 

An 8kW generator will max out at ~60-65A. The running draw of each A/C is ~14-15A which makes it possible to run 3 of them, but if they all decide to start at the same time the system will be overloaded and there will be substantial voltage drop. This is what what doing in the A/C's on our friend's MH.

Link to comment
Share on other sites

My coach has 2 acs plus the dash air. I have only ever found a need to run 1 ac at a time even in very hot weather. Not sure why any coach would need 3. Possibly the darker coaches soak up more heat from the sun? Mine also has dual pane windows...helps immensely for both AC season and heating season.