Hey you Solar Equipment Experts and users, I have a question:

I have a Renogy Rover 60 Amp MPPT Solar Charge Controller feeding my SOK 412 Amp Hour 12.8 Volt Lithium Battery Bank, has worked perfect two years using the Renogy FACTORY lithium charge parameter setting which charges around 14.4 Volts.

I want to add a second Renogy Rover 20 Amp MPPT Charge Controller fed by another new panel ALSO SET at its same factory Lithium 14.4 Volt charge.

QUESTION with the outputs of both controllers,,,, identical other than size,,,, each at same factory charge rate of 14.4 Volts,,, feeding the same battery bank,,,  WORK OKAY AND EACH ADD CHARGING AMPS AND NOT FIGHT EACH OTHER ????

The reason I asked is I've seen 2 or even 3 charge controllers feeding a common battery bank and they worked TOGETHER and added charging amps, however I've been told by someone (supposed to know??) NOT to do this ????? I could series up panels, but my Renogy may not be capable of either the new total higher voltage or all the charging amps capacity my panels could deliver grrrrrrrr A new single bigger Volts and Current  MPPT ???

PS I could bump up EACH controller to 14.6 charging voltage but that's NOT my issue/question, Im concerned if they will work TOGETHER add charging amps and not interfere with each other ???

Thanks yall

John T

Edited by oldjohnt
Link to comment
Share on other sites

I have 2 Epever controllers and an Outback controller.  On occasion I will add the inverter/charger.  It works great.  Since the controllers are voltage regulated these keep the voltage needed or as high of voltage as the solar will support.  On occasion I have seen one controller working a little harder than another but I don't see that as a problem.  Each controller has different panels and the panel voltages vary significantly. 

Randy

2001 Volvo VNL 42 Cummins ISX Autoshift

Link to comment
Share on other sites

I would also like to add that as long as the charge controllers combined are within the  total amp capacity of the batteries I cannot think of a reason that this isn't a good idea.  With LifeP04  it would take a really powerful charger or solar array to push to many amps.  The controllers I use are all different sizes. 

Randy

2001 Volvo VNL 42 Cummins ISX Autoshift

Link to comment
Share on other sites

I have 2 all in one units. So two different mppt controllers feeding same battery pk. Works fine. Also both units have dual mppt controllers so I could have 4 feeding same pk if more solar added.

Edited by GlennWest

2003 Teton Grand Freedom towed with 2006 Freightliner Century 120 across the beautiful USA welding pipe.https://photos.app.goo.gl/O32ZjgzSzgK7LAyt1

Link to comment
Share on other sites

UPDATE  I finally had a good bright day to pull the RV out into the sun to see what happens. With BOTH the 60 Amp Renogy hooked to 4 panels and the 20 Amp Renogy hooked to its own new separate panel (for necessary reasons) ALL TO THE SAME LITHIUM BATTERY BANK.......BOTH set at the same factory lithium charging voltage and parameters.......

BOTH were pumping charging amps into the battery,,,,,Neither changed + or - of what charging amps they were contributing together versus if one or the other was shut off..............

NOTE it was Renogy Technical Support that told me doing that was NOT recommended... I can envision the case where if two controllers had different charging algorithms there could be conflict issues, none appear in my case.. 

 For now Im leaving things as is, its not broke (for now) so Im NOT gonna fix it lol

Thanks gang

John T 

Link to comment
Share on other sites

As you found, there are no issues running multiple charge controllers in parallel to a single battery bank.  I currently have three charge controllers going to my single battery bank.  I prefer controllers that can be networked to talk to one another to better coordinate charging, but this isn’t required.  The only thing you have to pay attention to is the battery max charge rate.  Every battery manufacturer has a recommended charge rate (how many amps the battery can accept).  You do not want to exceed this number or you could damage the battery (if AGM/Lead Acid) or cause the BMS to kick in and shut down charging (if Lithium).

2000 Kenworth T2000 w/ Cummins N14 and autoshift
2017 DRV Mobile Suite 40KSSB4 with factory mods, dealer mods and personal mods - now in the RV graveyard
2022 DRV Full House MX450 with customized floor plan
2018 Polaris RZR Turbo S (fits in the garage)
2016 Smart Car (fits in the garage or gets flat towed behind the DRV when the RZR is in the garage)
My First Solar Install Thread
My Second Solar Install Thread & Photos and Documents Related to the build
My MX450's solar, battery and inverter system - my biggest system yet!

chadheiser.com      West Coast HDT Rally Website

event.png    

AZCACOIDIAKSMNMOMTNENVNMNDOKSDTNTXUTWYxlg.jpg

 

Link to comment
Share on other sites

14 hours ago, Chad Heiser said:

The only thing you have to pay attention to is the battery max charge rate.

  Thanks Chad, I'm good as far as that, my max charge rate is 100 Amps and I don't anticipate over 75/85 amps max. I had seen multiple controllers used before and didn't anticipate problems, especially with my two matched controllers, but when Renogy Tech Support recommended NOT to do this I was concerned which prompted my post. However, as an attorney and engineer I understand why the corporate lawyers insist on such things in manuals with big caution warnings like CONSULT AND FOLLOW NEC GUIDELINES etc. etc. fills a page lol

 I'm good to go and felt better after todays experimenting

  John T 

 

Edited by oldjohnt
Link to comment
Share on other sites

Join the conversation

You can post now and register later. If you have an account, sign in now to post with your account.

Guest
Reply to this topic...

×   Pasted as rich text.   Paste as plain text instead

  Only 75 emoji are allowed.

×   Your link has been automatically embedded.   Display as a link instead

×   Your previous content has been restored.   Clear editor

×   You cannot paste images directly. Upload or insert images from URL.

Loading...
×
×
  • Create New...