Help me understand this Electrical Problem


jeanhoyle

Recommended Posts

Hopefully someone can help me understand what is happening with my electric.

 

For the past three weekends ( Saturday and Sunday) our 50 amp Surge Guard Model 34850 has been tripped by a high voltage reading on one leg of the 50 amp pedestal at our site. The voltage readout has been as high as 132 volts on l-1 and 128 volts on l-2. When our Surge Guard senses more than 130 volts it will turn off. I understand it is for the safety of my electronics on board.

 

The service here is a 200 amp box with a 50 amp 30 amp and 20 amp outlets.

 

What can cause High Voltage on one leg of our 50 amp service? I can understand what would cause low current but not High Voltage.

 

We turned in a service call to the local electric company and they sent out a technician and he was completely perplexed. He Blamed it on false readings from our Surge Guard. We did convince him to put a monitor device at the meter. It is currently making a recording of the quality of power coming to the meter. Multimeter readings show the same as the Surge Guard.

Jeanie and John

Ford F-250 super crew

Americana 34/35 GS (it's a Forest River Cardinal with extras)

Link to comment
Share on other sites

A poor Neutral connection can cause this. The Neutral is in the center between the two Hot Legs (electrically). If the Neutral is poor, a current load on one of the legs will draw its voltage down with the other leg climbing. The rise on the unloaded leg voltage is faster than the voltage drop on the loaded leg. With a good Neutral the changes on one Hot leg are not reflected on the other.

 

The result is the EMS trips on High Voltage. This is one of those problems that a simple meter cannot find because the condition only happens under load.

 

The Neutral gets tied to Ground nearest to power station. If this your residence, the Neutral to ground connection is at the Entrance Power Panel.

 

Don't skip suspecting the receptacle and the plug.

Please click for Emails instead of PM
Mark & Dale
Joey - 2016 Bounder 33C Tige - 2006 40' Travel Supreme
Sparky III - 2021 Mustang Mach-e, off the the Road since 2019
Useful HDT Truck, Trailer, and Full-timing Info at
www.dmbruss.com

Link to comment
Share on other sites

A poor Neutral connection can cause this. The Neutral is in the center between the two Hot Legs (electrically). If the Neutral is poor, a current load on one of the legs will draw its voltage down with the other leg climbing. The rise on the unloaded leg voltage is faster than the voltage drop on the loaded leg. With a good Neutral the changes on one Hot leg are not reflected on the other.

 

The result is the EMS trips on High Voltage. This is one of those problems that a simple meter cannot find because the condition only happens under load.

 

The Neutral gets tied to Ground nearest to power station. If this your residence, the Neutral to ground connection is at the Entrance Power Panel.

 

Don't skip suspecting the receptacle and the plug.

Nice answer.

Rex & Karen

Libre y pobre en La Casa Rodante

Link to comment
Share on other sites

That makes sense, but the first time it started was at 2:30 or 3:00 AM. When everything was turned off there should not have been a current load.

Jeanie and John

Ford F-250 super crew

Americana 34/35 GS (it's a Forest River Cardinal with extras)

Link to comment
Share on other sites

Last time I had that problem it was the power company regulation. If it were a neutral problem one leg would go very high and the other would go very low when a load was applied to the leg. Like 160 and 80.

 

I think it is an issue with your electric provider and you need to call them.

Steve and Joy

Amateur Radio Operator WZ1T . . .  Flex 6600 M,  Flex PGXL, Flex TGXL, 

2014 Itasca Suncruiser 38Q . . . Lincoln MKX Toad


The Kids . . . Yogi the Yorkie  passed 10/20/2018. . . Cookie the Chihuahua passed 11/30/2017 . . . Cooper the Aussie Doodle passed 3/10/2020

Abbie  and Abel  the Doodles . . . Brother and Sister Born 02/02/2020   . . . Lucy the Yorkie . . . and Axel  . . .The Bernie Doodle

 

Where We Are Now

Link to comment
Share on other sites

A poor Neutral connection can cause this. The Neutral is in the center between the two Hot Legs (electrically). If the Neutral is poor, a current load on one of the legs will draw its voltage down with the other leg climbing. The rise on the unloaded leg voltage is faster than the voltage drop on the loaded leg. With a good Neutral the changes on one Hot leg are not reflected on the other.

This is what electricians call a "floating neutral" and is caused by a difference in resistance between the neutral and one side or the other of your power supply. The two legs of your supply (or phases) are not from different sources but actually are supplied by what is called a center tapped transformer, with one hot leg tied to one end and the other hot tied to the opposite and the neutral is actually connected into the center of the transformer secondary.

Centre-Tapped-Transformer.jpg

When some resistance to current flow is introduced into one side or this source only and not on the other side it causes the neutral to float, or electrically move toward one side or the other of the diagram and thus cause the 240V across the entire circuit to shift and be higher on one leg and lower on the other. When your supply from the power company is on the specified 240V, a minimal amount of this shifting will not be noticed because both legs will remain within the specified +/- 10% but as the source voltage moves toward either limit the result becomes more quickly noticed by your Surge-Guard. The supply from the power company is not actually a constant voltage but is typically at +/- 5v or between 115v and 125v and SG shuts you down at 108v or 132v on either leg.

 

In this example, Va and Vb are each one 120V leg while Vtotal is the 240V supply that in your house would be sent to the electric stove or dryer.

Good travelin !...............Kirk

Full-time 11+ years...... Now seasonal travelers.
Kirk & Pam's Great RV Adventure

            images?q=tbn:ANd9GcQqFswi_bvvojaMvanTWAI

 

Link to comment
Share on other sites

I'm going with Ranger Smith in answer #5.Both legs are going high L1--128 and L2 -- 130+.

Both may well be high, and throw in a low level of float you get exactly what he has. But Ranger's is an example that is clearly a situation of float. "Like 160 and 80." A very small amount of float is allowable but as voltages go either high or low the impact on the SG kicks in.

Good travelin !...............Kirk

Full-time 11+ years...... Now seasonal travelers.
Kirk & Pam's Great RV Adventure

            images?q=tbn:ANd9GcQqFswi_bvvojaMvanTWAI

 

Link to comment
Share on other sites

Archived

This topic is now archived and is closed to further replies.

RVers Online University

campgroundviews.com

RV Destinations

Find out more or sign up for Escapees RV'ers Bootcamp.

Advertise your product or service here.

The Rvers- Now Streaming

RVTravel.com Logo



×
×
  • Create New...