Erik Green Posted March 24, 2022 Report Share Posted March 24, 2022 Good Morning All, We are currently parked outside okc (I am away for a few days for work) the RV is plugged in to a 30 amp service. The dual victrons are set to split phase 180 auto and not switched as group. THe power completely shut off yesterday, my wife checked primary fuses and tried resetting multiplus and power cycled everything. Power no longer passing through and Leg one will not re-engage inverting and other multiplus seems to function to charge only. I have run out of ideas. Trying to come up with something my wife can do to get power back on. any help or ideas would be greatly appreciated thanks! Quote 2021 Grand Design Solitude 380FL 42 Ft 2015 Ford F450 Platinum Link to comment Share on other sites More sharing options...
Chad Heiser Posted March 25, 2022 Report Share Posted March 25, 2022 Did it work at all when plugged into this 30 amp pedestal prior to the failure? Quote 2009 Volvo 670 with dinette/workstation sleeper - Walter 2017 DRV Mobile Suite 40KSSB4 with factory mods, dealer mods and personal mods - now in the RV graveyard 2022 DRV Full House MX450 with customized floor plan 2018 Polaris RZR Turbo S (fits in the garage) 2016 Smart Car (fits in the garage or gets flat towed behind the DRV when the RZR is in the garage) My First Solar Install Thread My Second Solar Install Thread & Photos and Documents Related to the build My MX450's solar, battery and inverter system - my biggest system yet! chadheiser.com West Coast HDT Rally Website Link to comment Share on other sites More sharing options...
Erik Green Posted March 28, 2022 Author Report Share Posted March 28, 2022 It was, I figured it out, unfortunately my wife had to go without power for two days. It over heated and melted the battery shutoff. It was passing through power on one leg and the other inverter was pulling too many amps/watts? through the other leg didn't blow the 300 amp fuse though. Upgrading to 4/0 wire but I am still not sure how to properly hook up my system on a 30 amp to prevent that in the future. Quote 2021 Grand Design Solitude 380FL 42 Ft 2015 Ford F450 Platinum Link to comment Share on other sites More sharing options...
Chad Heiser Posted March 29, 2022 Report Share Posted March 29, 2022 Without knowing how your system is wired, I can only speculate as to why the switch overheated. Generally though, it is caused by resistance (which generates heat). In a 12 volt dual inverter system, all your battery and inverter cables should be 4/0 cable. That switch appears to be a Blue Sea 3000 HD switch. It is rated for 600 amps. It wasn’t the amps that killed that switch, it was resistance/heat. Quote 2009 Volvo 670 with dinette/workstation sleeper - Walter 2017 DRV Mobile Suite 40KSSB4 with factory mods, dealer mods and personal mods - now in the RV graveyard 2022 DRV Full House MX450 with customized floor plan 2018 Polaris RZR Turbo S (fits in the garage) 2016 Smart Car (fits in the garage or gets flat towed behind the DRV when the RZR is in the garage) My First Solar Install Thread My Second Solar Install Thread & Photos and Documents Related to the build My MX450's solar, battery and inverter system - my biggest system yet! chadheiser.com West Coast HDT Rally Website Link to comment Share on other sites More sharing options...
Erik Green Posted March 29, 2022 Author Report Share Posted March 29, 2022 Yep totally agree Chad, I hadn't gotten to replacing the wiring from my original install. I usually am at the trailer so I was monitoring the consumption, but when I was gone my wife ran a few to many devices (dryer/elec water heater/ and then some that burnt it out. here is my new drawing with 4/0 for all battery/inverter wires. I am open to any feedback. Also any advice on how to properly set up the system to run on 30 amp would be greatly appreciated. Quote 2021 Grand Design Solitude 380FL 42 Ft 2015 Ford F450 Platinum Link to comment Share on other sites More sharing options...
Lance A Lott Posted March 29, 2022 Report Share Posted March 29, 2022 I would be hesitant to run as much as you indicated might have been running on 30 amps but more so if it's a 50 amp system using a 30 amp adapter. The multi plus might have been trying to make up the extra needed. Quote Link to comment Share on other sites More sharing options...
Erik Green Posted March 29, 2022 Author Report Share Posted March 29, 2022 Yea no doubt it was a lot of power. Roughly 1500 Watts but this should be more than manageable with the system given proper gauge cabling ie 4/0. the thing I am not sure of is how the Victrons should run while connected to 30 amp. I had removed "switch as group" and it seemed to do ok, until the cables melted the switch. 6AWG cables probably the cause there. But is that the appropraite configuration for dual multis when hooked up to a 30 amp pedestal. Quote 2021 Grand Design Solitude 380FL 42 Ft 2015 Ford F450 Platinum Link to comment Share on other sites More sharing options...
Chad Heiser Posted March 29, 2022 Report Share Posted March 29, 2022 3 hours ago, Erik Green said: Yea no doubt it was a lot of power. Roughly 1500 Watts but this should be more than manageable with the system given proper gauge cabling ie 4/0. the thing I am not sure of is how the Victrons should run while connected to 30 amp. I had removed "switch as group" and it seemed to do ok, until the cables melted the switch. 6AWG cables probably the cause there. But is that the appropraite configuration for dual multis when hooked up to a 30 amp pedestal. Yes, if you are running split phase dual multiplus inverters, you need to uncheck the switch as group checkbox in the configuration. If you leave that box checked and plug into anything that does not provide split phase power (basically anything less than a 50 amp pedestal) the system won’t pass power through. With the switch as group unchecked, then power will pass through the inverter on L1 and the inverter on L2 will invert at 180 degrees out of phase to L1 to provide 120/240 volt power to the rig. If you only had 6 AWG wire running through the blue sea switch, that is the reason it melted. I’m surprised it didn’t start a fire in your rig. As I explained above, your L2 inverter was inverting to provide power to all loads on the L2 side of the panel box because the rig was plugged into a 30 amp (single phase) pedestal. That could have been up to 3000 watts of power coming from the inverter on L2. In a 12 volt system, that is upwards of 230 amps of DC power going over those cables. That is way too much for 6 AWG wire. When you are on 50 amp shore power, both inverters pass through 120 volt power and the only power to/from the batteries to the inverter is whatever charge current the inverters are supplying. Those inverters can charge at up to 120 amps each. Hopefully you have turned the chargers to a lower amperage setting than that until you upgrade the wiring. That much current could also cause a fire if going through 6 AWG wire. If the batteries are always at or near full, then the inverters won’t send that much charge current to them, but if they are low the inverters will send as much charge current as they can to recharge them. You should not be using your system at all if it is wired with 6 AWG wire on the 12 volt side. It needs to be rewired as soon as possible before you have a catastrophic failure. Quote 2009 Volvo 670 with dinette/workstation sleeper - Walter 2017 DRV Mobile Suite 40KSSB4 with factory mods, dealer mods and personal mods - now in the RV graveyard 2022 DRV Full House MX450 with customized floor plan 2018 Polaris RZR Turbo S (fits in the garage) 2016 Smart Car (fits in the garage or gets flat towed behind the DRV when the RZR is in the garage) My First Solar Install Thread My Second Solar Install Thread & Photos and Documents Related to the build My MX450's solar, battery and inverter system - my biggest system yet! chadheiser.com West Coast HDT Rally Website Link to comment Share on other sites More sharing options...
Erik Green Posted March 29, 2022 Author Report Share Posted March 29, 2022 100% thanks Chad, yea luckily my wife smelled something off (heat shrink glue melting) and shut it down. All parts are delivered to our next campground so I can start the retrofit tomorrow. Also as shown in the diagram I am converting my 8 battery bank from 8 in parallel to 4 sets of two. Everything will be in 4/0 once I convery it. Also one other error I made on my initial install was putting the 12v dc out after the blue sea switch on leg two. So all DC + AC was pulling through that same 6awg wire. As I mentioned I had been keeping a close eye on consumption, this is the first time I was away that we werent on 50 amp/pass through power. glad it wasnt worse! Quote 2021 Grand Design Solitude 380FL 42 Ft 2015 Ford F450 Platinum Link to comment Share on other sites More sharing options...
Chad Heiser Posted March 30, 2022 Report Share Posted March 30, 2022 Good luck with the retrofit. I hope it all goes well. Quote 2009 Volvo 670 with dinette/workstation sleeper - Walter 2017 DRV Mobile Suite 40KSSB4 with factory mods, dealer mods and personal mods - now in the RV graveyard 2022 DRV Full House MX450 with customized floor plan 2018 Polaris RZR Turbo S (fits in the garage) 2016 Smart Car (fits in the garage or gets flat towed behind the DRV when the RZR is in the garage) My First Solar Install Thread My Second Solar Install Thread & Photos and Documents Related to the build My MX450's solar, battery and inverter system - my biggest system yet! chadheiser.com West Coast HDT Rally Website Link to comment Share on other sites More sharing options...