  1. Denny,

    I am sure I could install it. If I did I would rent a material lift for $75. The unit would cost me about $1,500. A few years ago I would not hesitate, but now I am 67 years old. I would also need to pick up the rental lift, get it in and out of my truck and return it. The unit weighs a little over 100 lbs. That's my top end of lifting at this point. The best bid I have so far (I always get three bids) is about $2,000 turn key. I could save about $400 if I do it myself but if I screw up and drop it or something it's on me. I am on the fence. I would love another win but I am not sure on this one. So simple yet it has its has some challenges. 

    I am thinking it over,

    Mike

  2. Denny,

    You are correct on both accounts.  It is locked up. I did a couple of other tests. I unhooked the compressor and set the stat to call for both heat and cool. The breaker did not trip. I also found I had 120 volts on the start relay so I think the control board is good. You are also correct it is a reversing valve.

    I really do appreciate all your responses. I wish I could have fixed it but not this time. Time to blow some cash, but you got to admit I did not just lay down and give up easily. 

    Mike

  3. Some of you folks thankfully have been trying to help me troubleshoot why my 2015 rooftop Dometic Heat Pump (#651816). The units fan will start but shortly after trips the breaker. I have gone through several things to try and diagnose what is causing it. As they say a picture is worth a thousand words words so a video showing testing the compressor for short to ground, replacing the breaker and testing and replacing the start and run capacitors may give you a better understanding of what I have tried. The fan and compressor relays are mounted on the control board so I can't just pull them off and just replace. I appreciate any help I can get. I am not an HVAC tech, just a home owner with enough skills to be very, very dangerous that likes to fix his own stuff and doesn't give up easily. Thanks again for any help you can provide, Mike

     

  4. Thanks again Denny,

    I did check for ground on each terminal and found no short to ground so I am thinking the problem is not the compressor.  I think that the starter relay is located on the control board. If the control board is bad I think I will have to replace the entire board. I could not see where I could remove any of the relays. Per your response I will also order a start cap. I have already ordered the run cap and a hard start cap. If it turns out to be the control board I might be able to use new capacitors down the road. I have two heat pumps on our rig. Again Thanks so much for all your help. Merry Christmas!

  5. My four year old Dometic Rooftop Heat pump is tripping the AC breaker. I can re-set the breaker and it will stay set until the thermostat calls for either cooling or heat. Up on the roof I can see the fan does not attempt to start nor does the compressor. I hear a very faint click and then the breaker trips. The fan spins freely and I can set the thermostat to just "Fan" and that does work. I cannot smell any kind of burning nor do I see and damage to any wires. I am thinking start capacitor either fan or compressor.

×
×