Victron MultiPlus II Inverter/Charger


Zulu

Recommended Posts

2 hours ago, Zulu said:

I'll go with the flow in this one. I think every schematic I've seen, including from Victron, shows the Class T fuse before the disconnect switch.

Also, after talking with a guy who used to do marine inverter installs, I updated my schematic and added an AC disconnect right before the inverter along with other changes people suggested.

Thanks folks!

2001-sea-view-battery-solar-inverter-wir

I fused the lead to existing 12v loads.  I also fused at the bus bar to protect all of the wires on it instead of near the connected circuits. Specifically the charge controller.  If the wires are short and safe it probably doesn't matter.

Edited by Randyretired

Randy

2001 Volvo VNL 42 Cummins ISX Autoshift

Link to comment
Share on other sites

1 hour ago, Randyretired said:

I also fused at the bus bar to protect all of the wires on it instead of near the connected circuits. Specifically the charge controller. 

I've been thinking about doing the same after seeing some of Chad's schematics like this one below that I believe uses a Victron Lynx Distributor instead of conventional bus bars:

GD-Solitude-ST310GK-2-Schematic-1.png

SKP #79313 / Full-Timing / 2001 National RV Sea View / 2008 Jeep Wrangler Rubicon
www.rvSeniorMoments.com
DISH TV for RVs

Link to comment
Share on other sites

When I really started getting into installing Victron products, I migrated from the Class T fuse for the batteries/inverter and individual resettable breakers for each branch circuit to the Lynx distributor.  It usually simplifies the wiring overall and gives a single place to look for fusing if something stops working.  It was also often cheaper in the long run.  I do still add additional circuit protection for the solar with a Midnite solar baby box and some MNEPV breakers though.

2000 Kenworth T2000 w/ Cummins N14 and autoshift
2017 DRV Mobile Suite 40KSSB4 with factory mods, dealer mods and personal mods - now in the RV graveyard
2022 DRV Full House MX450 with customized floor plan
2018 Polaris RZR Turbo S (fits in the garage)
2016 Smart Car (fits in the garage or gets flat towed behind the DRV when the RZR is in the garage)
My First Solar Install Thread
My Second Solar Install Thread & Photos and Documents Related to the build
My MX450's solar, battery and inverter system - my biggest system yet!

chadheiser.com      West Coast HDT Rally Website

event.png    

AZCACOIDIAKSMNMOMTNENVNMNDOKSDTNTXUTWYxlg.jpg

 

Link to comment
Share on other sites

  • 1 month later...

Victron MultiPlus II AC-IN fusing/circuit breaker

I've started wiring my RV for its eventual solar upgrade. As part of this process, I have to disconnect the AC panel input from the Transfer switch, and then run this Transfer switch output about 12 feet to my Victron MultiPlus II inverter. (They'll also be a similar AC run back into the AC panel.)

I was going to install a AC disconnect switch on the Transfer switch output going into the Victron inverter, but found this in the Victron MultiPlus II manual for the inverter's AC-In:

The AC input must be protected by a fuse or magnetic circuit breaker rated at 50A or less, and cable cross-section must be sized accordingly. (BOLD text by Victron)

This seems like a much better solution than an AC disconnect switch.

SKP #79313 / Full-Timing / 2001 National RV Sea View / 2008 Jeep Wrangler Rubicon
www.rvSeniorMoments.com
DISH TV for RVs

Link to comment
Share on other sites

I stumbled into this a while ago for a different project, maybe it will help with wire sizing.

NOTE: this is for DC currents.  the source is Engineering toolbox

1321152577_12wiregaugevsamps.jpg.7fabc03f6ea09b76e5ab7a88a81281aa.jpg

 

+++++++++++_____________________________________+++++++++++

2021 Ram 3500  2017 Arctic Fox 25W(to be traded??)
HAM guy (Ke7FIX), photography, woodworking (mostly sawdust),
Electronics Technician,  USAF DAV

Going where everyone has gone before

 

              event.png                                             

Link to comment
Share on other sites

Assuming your trailer is not hard wired to an electrical source, your AC in on the inverter is protected by the pedestal you plug the trailer into (and it’s breaker) and (since you said transfer switch) by the circuit breaker built into the generator (if you have an onboard generator).  There is no need to add an additional breaker.  There is no need for an AC shutoff switch either.  If you want to add one it won’t hurt, but there is no need for one.  I have seen some people add a bypass switch so the inverter can be cut out of the system in case it fails.  Personally for the very unlikely event of a complete inverter failure, I would simply remove the AC in and AC out wiring from the inverter and wire nut those lines together temporarily until the inverter was repaired.

2000 Kenworth T2000 w/ Cummins N14 and autoshift
2017 DRV Mobile Suite 40KSSB4 with factory mods, dealer mods and personal mods - now in the RV graveyard
2022 DRV Full House MX450 with customized floor plan
2018 Polaris RZR Turbo S (fits in the garage)
2016 Smart Car (fits in the garage or gets flat towed behind the DRV when the RZR is in the garage)
My First Solar Install Thread
My Second Solar Install Thread & Photos and Documents Related to the build
My MX450's solar, battery and inverter system - my biggest system yet!

chadheiser.com      West Coast HDT Rally Website

event.png    

AZCACOIDIAKSMNMOMTNENVNMNDOKSDTNTXUTWYxlg.jpg

 

Link to comment
Share on other sites

2 hours ago, Zulu said:

Yep. Were the failures you saw on Victrons?

There have been some failures with the Multiplus II push in AC connections posted on line.  Every one I have seen can be explained by improper installation by the DIY installer.  Follow the instructions and install the connections properly and you will have no issues.

2000 Kenworth T2000 w/ Cummins N14 and autoshift
2017 DRV Mobile Suite 40KSSB4 with factory mods, dealer mods and personal mods - now in the RV graveyard
2022 DRV Full House MX450 with customized floor plan
2018 Polaris RZR Turbo S (fits in the garage)
2016 Smart Car (fits in the garage or gets flat towed behind the DRV when the RZR is in the garage)
My First Solar Install Thread
My Second Solar Install Thread & Photos and Documents Related to the build
My MX450's solar, battery and inverter system - my biggest system yet!

chadheiser.com      West Coast HDT Rally Website

event.png    

AZCACOIDIAKSMNMOMTNENVNMNDOKSDTNTXUTWYxlg.jpg

 

Link to comment
Share on other sites

1 hour ago, Chad Heiser said:

There is no need to add an additional breaker.  There is no need for an AC shutoff switch either.  If you want to add one it won’t hurt, but there is no need for one.  I have seen some people add a bypass switch so the inverter can be cut out of the system in case it fails.  Personally for the very unlikely event of a complete inverter failure, I would simply remove the AC in and AC out wiring from the inverter and wire nut those lines together temporarily until the inverter was repaired.

I want a quick way to shut off the AC In to the inverter.

I’m still going with dual 50A breakers instead of a simple AC cut off as I’ve seen too many suspect pedestal breakers.

 

SKP #79313 / Full-Timing / 2001 National RV Sea View / 2008 Jeep Wrangler Rubicon
www.rvSeniorMoments.com
DISH TV for RVs

Link to comment
Share on other sites

1 hour ago, Chad Heiser said:

There have been some failures with the Multiplus II push in AC connections posted on line.  Every one I have seen can be explained by improper installation by the DIY installer.  Follow the instructions and install the connections properly and you will have no issues.

I’ve started using ferrules which go a long way to making wiring more secure.

ferules.jpg

SKP #79313 / Full-Timing / 2001 National RV Sea View / 2008 Jeep Wrangler Rubicon
www.rvSeniorMoments.com
DISH TV for RVs

Link to comment
Share on other sites

I felt this needed bring up. Yes ferrules is the way to go. Failures I saw are melted connections. I am not a fan of push in connections. Wished Victron hadn't went that way. https://m.facebook.com/groups/2589581644599315/permalink/3831170990440368/

Edited by GlennWest

2003 Teton Grand Freedom towed with 2006 Freightliner Century 120 across the beautiful USA welding pipe.https://photos.app.goo.gl/O32ZjgzSzgK7LAyt1

Link to comment
Share on other sites

here is a source I use at work for Ferrules:
www.ferrulesdirect.com

That site has a huge selection of many types of terminal ends, ferrules and zip ties.

Make sure you use the correct tool to crimp them on, or a poor crimp could result in a poor connection that heats up under high current and melts insulation. Heat is wasted energy and depending on what is near by, could cause a fire.

 

+++++++++++_____________________________________+++++++++++

2021 Ram 3500  2017 Arctic Fox 25W(to be traded??)
HAM guy (Ke7FIX), photography, woodworking (mostly sawdust),
Electronics Technician,  USAF DAV

Going where everyone has gone before

 

              event.png                                             

Link to comment
Share on other sites

This is the one I use, showing not available on amazon but may be elsewhere. And there are other brands also.

 

https://www.amazon.com/gp/product/B07212XQTV/ref=ppx_yo_dt_b_search_asin_title?ie=UTF8&psc=1

Back on the road again in a 2011 Roadtrek 210P

2011 Tahoe 4x4, 2006 Lexus GX470, 2018 Ranger XP1000, 2013 RZR 570LE
http://finallynewellin.blogspot.com/

 

458863254_cabinavatarcopy.jpg.7751792e372f5959d079d77730f9290d.jpg

 

 

Link to comment
Share on other sites

14 hours ago, Zulu said:

I want a quick way to shut off the AC In to the inverter.

I’m still going with dual 50A breakers instead of a simple AC cut off as I’ve seen too many suspect pedestal breakers.

 

Nothing wrong with that.  I do it for all my dual inverter installations, but it is more because I need to split the four wire (L1, L2, N, G) feed into a six wire (L1, N, G and L2, N,G) feed and back.  I use small (70 amp) load centers with 50 amp double pole breakers to make the split and then re-combine back to four wire.  One box/breaker goes on the AC input side of the inverters and the other goes on the AC output side of the inverters.  For your installation you would just need one on the input side to do what you want.

2000 Kenworth T2000 w/ Cummins N14 and autoshift
2017 DRV Mobile Suite 40KSSB4 with factory mods, dealer mods and personal mods - now in the RV graveyard
2022 DRV Full House MX450 with customized floor plan
2018 Polaris RZR Turbo S (fits in the garage)
2016 Smart Car (fits in the garage or gets flat towed behind the DRV when the RZR is in the garage)
My First Solar Install Thread
My Second Solar Install Thread & Photos and Documents Related to the build
My MX450's solar, battery and inverter system - my biggest system yet!

chadheiser.com      West Coast HDT Rally Website

event.png    

AZCACOIDIAKSMNMOMTNENVNMNDOKSDTNTXUTWYxlg.jpg

 

Link to comment
Share on other sites

14 hours ago, Zulu said:

I’ve started using ferrules which go a long way to making wiring more secure.

ferules.jpg

I also recently started using ferrules.  As a matter of fact I just got a shipment of 6 awg ferrules from ferrulesdirect.com today.  They help make it easier to get the stranded wire into the connections and should also make a better connection in the inverter.

2000 Kenworth T2000 w/ Cummins N14 and autoshift
2017 DRV Mobile Suite 40KSSB4 with factory mods, dealer mods and personal mods - now in the RV graveyard
2022 DRV Full House MX450 with customized floor plan
2018 Polaris RZR Turbo S (fits in the garage)
2016 Smart Car (fits in the garage or gets flat towed behind the DRV when the RZR is in the garage)
My First Solar Install Thread
My Second Solar Install Thread & Photos and Documents Related to the build
My MX450's solar, battery and inverter system - my biggest system yet!

chadheiser.com      West Coast HDT Rally Website

event.png    

AZCACOIDIAKSMNMOMTNENVNMNDOKSDTNTXUTWYxlg.jpg

 

Link to comment
Share on other sites

  • 4 months later...

I bought a solar package the inlcudes a new Victron MultiPlus-II inverter for my 2009 Tiffin Phaeton 36QSH. The old Xantrex RV2012GS had two 30-amp (one hot wire) conductors as inputs and two 30-amp conductors on the output side. The Victron expects one 50-amp (two hot wires) input and output. Can I combine the 30-amp conductors by joing the two neutrals together? Some people say that combining neutrals will cause the GFCI circuits to trip. My solar dealer was clueless and I can't contact Victron directly.

Link to comment
Share on other sites

3 hours ago, Elmo1706 said:

I bought a solar package the inlcudes a new Victron MultiPlus-II inverter for my 2009 Tiffin Phaeton 36QSH. The old Xantrex RV2012GS had two 30-amp (one hot wire) conductors as inputs and two 30-amp conductors on the output side. The Victron expects one 50-amp (two hot wires) input and output. Can I combine the 30-amp conductors by joing the two neutrals together? Some people say that combining neutrals will cause the GFCI circuits to trip. My solar dealer was clueless and I can't contact Victron directly.

So you have a 30 amp rig? If so just wire in L1, Neutral and ground. Leave L2 disconnected. You will just always have 30 amp. 

Edited by GlennWest

2003 Teton Grand Freedom towed with 2006 Freightliner Century 120 across the beautiful USA welding pipe.https://photos.app.goo.gl/O32ZjgzSzgK7LAyt1

Link to comment
Share on other sites

Join the conversation

You can post now and register later. If you have an account, sign in now to post with your account.

Guest
Reply to this topic...

×   Pasted as rich text.   Paste as plain text instead

  Only 75 emoji are allowed.

×   Your link has been automatically embedded.   Display as a link instead

×   Your previous content has been restored.   Clear editor

×   You cannot paste images directly. Upload or insert images from URL.

Loading...
×
×
  • Create New...