Sounds like the switch is bad

Steve and Joy

Amateur Radio Operator WZ1T . . .  Flex 6600 M,  Flex PGXL, Flex TGXL, 

2014 Itasca Suncruiser 38Q . . . Lincoln MKX Toad


The Kids . . . Yogi the Yorkie  passed 10/20/2018. . . Cookie the Chihuahua passed 11/30/2017 . . . Cooper the Aussie Doodle passed 3/10/2020

Abbie  and Abel  the Doodles . . . Brother and Sister Born 02/02/2020   . . . Lucy the Yorkie . . . and Axel  . . .The Bernie Doodle

 

Where We Are Now

Link to comment
Share on other sites

Does it do anything at all when you press the switch? And click or sound of any type? When you say that you jump the solenoid, do you mean similar to starting a car with a screwdriver like we did years ago? Or may jump with another battery? Could it be the battery is the problem? When you get it to start, does in then continue to run and supply 120V power? 

Good travelin !...............Kirk

Full-time 11+ years...... Now seasonal travelers.
Kirk & Pam's Great RV Adventure

            images?q=tbn:ANd9GcQqFswi_bvvojaMvanTWAI

 

Link to comment
Share on other sites

Check the connection for the switch to be sure it is wired correctly and then check for power to it and from it. 

2005 Freightliner Century S/T, Singled, Air ride ET Jr. hitch
2019 46'+ Dune Sport Man Cave custom 5th wheel toy hauler
Owner of the 1978 Custom Van "Star Dreamer" which might be seen at a local car show near you!

 

Check out http://www.hhrvresource.com/

for much more info on HDT's.

Link to comment
Share on other sites

If this post is against rules moderator can delete. Go to smokestack.com, scroll down to onan site. Have model, serial and spec number. Ask your question. These are sharp  guys on onan's.

2002 Beaver Marquis Emerald   C-12 Cat 505 HP

2014 Volvo 630 D-13 I Shift SOLD

2017 New Horizons SOLD

 

 

 

 

Link to comment
Share on other sites

6 hours ago, DJohns said:

If this post is against rules moderator can delete. Go to smokestack.com, scroll down to onan site. Have model, serial and spec number. Ask your question. These are sharp  guys on onan's.

The link for the SmokeStak.com (no 'c') Onan Forum is:

https://www.smokstak.com/forum/forums/onan-generators.1/

Dutch
2001 GBM Landau 34' Class A
F-53 Chassis, Triton V10, TST TPMS
2011 Toyota RAV4 4WD/Remco pump
ReadyBrute Elite tow bar/brake system

Link to comment
Share on other sites

Ok, yes it runs after I jump the solenoid and what I do is give 12volt power to the S side of the solenoid and it starts to turn over and when I take my jumper off it fires and runs.. it sounds good and it produces 120 volt power to my RV. Then I try the switch again to shut it off and it won't do a thing. How I shut it off is pull the fuse on the gen-set  and it dies.. I cannot get the switch to do anything. I have changed out the relays that are there and I've swapped out the switch with another gen-set just like mine... I've traced the wiring and it appears to be all right... so im stuck with what to do next.

Link to comment
Share on other sites

I would suggest contacting this company. I have been to there business many years ago.     Well I cannot copy and paste there site. It is Flight Systems.   Search them on the net.

  Ask for tech support and they should be able to help you.

 

   I may have Onan service manuals.  Later this morning I will see if my tech manual has a wiring diagram.

 

 

  Vern in a T-shirt 

Link to comment
Share on other sites

   So I went to a service document from Flight Systems and the apparently the Escapees site will not let me copy and paste.

  Or where i am getting the info will not let me copy and paste.

 

  Send me a private message with a email and I will send you the info

 

 

    Vern in a T-shirt 

Link to comment
Share on other sites

RV GENERATOR TROUBLESHOOTING GUIDE
A Service of
FLIGHT SYSTEMS
207 Hempt Road • Mechanicsburg, PA 17050
Ph: 717 590 7330 Fax: 717 590 7327 www.flightsystems.com
CONTENTS
RV Generator Troubleshooting Overview 1 RV Generator FAQs 5
Onan® RV Generator Charts:
Applications Chart 8 Test Information for Troubleshooting
9Regulator Pin Assignment Chart 10 Control Board P/N Supersedence 10 Oil Press/Level Switch Locations 10
Onan® RV Generator Control Board & Regulator Illustrations
Voltage Regulator Mating Plug 11 300-2784/2943 Control Board (Onan® Original) 11 300-2784/2943 Control Board (F.S. Replacement)
12
300-3056/3687 Control Board 12 300-3763/3764 Control Board 13
        300-4901 Control Board 300-4902 Control Board 300-4320 Control Board 300-4155 Control Board
13 14 14 15
Issued 6/08; Revised 1/09

RV GENERATOR TROUBLESHOOTING OVERVIEW HOW DOES MY RV GENERATOR WORK?
Note: While this troubleshooting guide is applicable to most makes of RV Gen Sets, there are many specific refer- ences to particular Onan® Models as these widely used RV Generators are the brand we (Flight Systems) provide replacement control boards, voltage regulators and test equipment (the G-MAN) for.
What the Engine Control Board Does
The engine control board or module controls the ignition, fuel pump, fuel solenoid (if equipped), field flash and starter. On LP models, it controls the flow of LP gas to the throttle body. Some models prevent the engine from starting if there is insufficient oil quantity. Some models prevent continued running if there is insufficient oil pressure. See Trouble- shooting Chart. NOTE: On models equipped with electronic governors (BGM, NHM Spec. B and later, 300-3764 control board), the oil pressure signal to the control board comes from the governor module. Additionally, most models require a voltage from the generator to keep the engine running once it has started. See Troubleshooting Chart. All controls terminate cranking and lock out the starter after the engine has started. The battery charging circuit is part of the control board on some models, and external on others. NOTE: The controls used on Models KY (Spec. J), KYD (Spec. A), HGJAB and HGJAC are microprocessor-based and combine the functions of the engine control and regulator in one module (300-5046, 327-1413 and 300-5374). Because these modules are difficult or impossible to access without special tools, they are not covered in these instructions.
What the Regulator Does
When the generator is first started, the regulator receives the field flash voltage from the control board and applies it to the generator field (rotor) to initiate AC voltage buildup in the stator. After the generator output voltage builds up, the regulator maintains it nearly constant (within a few volts of 120 VAC) under conditions of varying load. It does this by sensing the 120 volts and constantly adjusting the DC field (rotor) voltage up or down, as needed. For example, if you turn on a light, the regulator would respond by increasing the field voltage only slightly to compensate for the added load. If you turn on a microwave oven or an air conditioner, the regulator would increase the field voltage by a much larger amount, in proportion to the heavier load. The regulator has a built-in protection circuit that reduces the output voltage of the generator if the engine is running too slow. The purpose of this feature is to protect your appliances from receiving full voltage at the lowered frequency, as this can cause damage to motors and transformers.
What the Bridge Rectifier Does
The Bridge Rectifier is found on RV generators that do not have an electronic voltage regulator. This will typically be found on BGE / NHE generators spec A-E. It serves two major functions, field flash and field (rotor) voltage supply. Upon starting, the control board provides 12 volts DC to the field windings via the + terminal of the rectifier. Once oil pressure comes up another set of relays closes and opens accordingly, on the control board, and then the rectifier begins to work. It now takes sensed voltage from the regulating transformer on the AC leads and rectifies it to DC voltage on
the + and – terminals. This is now the DC voltage that supplies the rotor of the generator.
Normal Starting Sequence
This is what normally happens when you start your genset. Pressing and holding the start switch causes the control board to send 12 volts to the ignition, fuel pump, choke heater, start solenoid and field flash circuits. The engine then cranks and starts. Oil pressure and generator voltage build up within 1-2 seconds. This causes the control board to keep sending 12 volts to the ignition, fuel pump and choke heater while cutting off 12 volts to the starter solenoid and field flash circuits. The start switch can then be released and the engine keeps running. Some models differ slightly in operation. On models equipped with magneto ignition (KV, Spec. C-F; KY, Spec. A-E), the control board un-grounds the magneto kill circuit. Model KY, Spec. B-E uses a fuel solenoid in addition to the fuel pump. Models fueled by LP gas use a fuel shutoff solenoid valve instead of a fuel pump. Several conditions can prevent the engine from starting/ running and are covered under Troubleshooting.
Normal Stopping Sequence
This is what happens when you stop your genset. Pressing and holding the stop switch for a few seconds causes the control board to cut off the 12 volts to the ignition and fuel pump (and/or fuel solenoid valve) causing the engine to stop. On models equipped with magneto ignition, the control board grounds the magneto kill circuit. Several condi- tions can cause the engine to stop by itself and are covered under Troubleshooting.
  1

TROUBLESHOOTING
Determine the control board part number from the board or from the Application Chart, then refer to the Troubleshoot- ing Chart for test information specific to that board. This troubleshooting guide assumes that the person doing the work has basic mechanical skills and is familiar with electrical troubleshooting procedures using a multi-meter. Having a practical knowledge of RV generators is helpful, but not absolutely necessary. DISCLAIMER: Generator servicing can present certain hazards such as cuts, burns, electric shock, fire, and exposure to exhaust fumes. Take suitable precautions. Flight Systems will not assume any liability for personal injury or damage to equipment or property as a result of using this Troubleshooting Guide.
Getting the Engine Running
Before any evaluation of the controls, regulator or generator can proceed, the Onan engine must have oil and fuel, be in running condition and the 12-volt battery charged. The electronic governor, 151-0752, on Models BGM and NHM, Spec B and later, must be functioning properly. This guide does not cover engine maintenance and repair procedures (please refer to the applicable Onan Service Manual for this information). The most common engine problems are caused mainly by lack of use and/or lack of regular monthly exercise and include the following:
• Low battery voltage because of insufficient charge, worn out battery, faulty cables (partly broken or corroded) or poor connections, resulting in slow cranking and hard starting.
• Old or contaminated fuel that has gummed up the lines, fuel filter and carburetor. This can cause clogged jets (mix- ture too lean) and/or a stuck carburetor float resulting in an improper mixture (too rich or too lean) or flooding.
• Weak spark and/or fouled spark plug(s) causing hard starting and rough running.
• Stuck automatic choke causing an excessively rich mixture and smoking.
• Stuck oil pressure switch causing shutdown as soon as the start button is released.
• Dirty air filter, causing an excessively rich mixture and smoking.
• Low oil level preventing starting on models equipped with low oil level switch.
• Wiring harness damage from rodents chewing on the wires.
• Corrosion of control board or connections from salty air or road chemicals.
FOLLOW THESE STEPS:
1. CHECK OIL Check engine oil level before starting.
2. GAIN ACCESS Remove panel or cover to gain access to the control board. Some disassembly may be required. The exact procedure depends on the model.
3. CHECK BATTERY VOLTAGE Connect the negative voltmeter lead to GROUND and the positive lead to the positive battery cable on the starter solenoid and read the battery voltage. The same reading should be obtained at the BATTERY POSITIVE pin of the control board. A fully charged battery in good condition should read 12.6 to 12.8 VDC. Charge the battery if necessary.
CHECK CRANKING Try to start the engine. If it does not crank, check the control fuse (5A Slo Blo, except models with electronic governor 10A). If the fuse is good, jumper the positive battery post to the coil terminal on the start so- lenoid. If the engine cranks, there is a poor connection, wiring damage or the control board is defective. If the engine cranks when the BATTERY POSITIVE pin is jumpered to the START SOLENOID pin on the control board, the board is defective. NOTE: The battery voltage should not go below 9.5 VDC during cranking.
 2

2. CHECK SPARK If the engine cranks but does not start, remove a spark plug and check for spark during cranking (spark plug must be grounded). Temporarily jumper the ignition coil positive to the starter solenoid positive termi- nal, or jumper the BATTERY POSITIVE pin to the IGNITION pin on the control board. If you now have spark, there is a poor connection, wiring damage or the control board is defective. To determine if it is the control board, check for 12 volts at the IGNITION pin during cranking. Other problems such as dirty /worn points or a defective coil can cause loss of spark. On models where the oil level switch is hard-wired to the magneto (KV Spec. C-F, KVC and KVD), low oil level or a stuck switch will inhibit the spark and prevent starting. On these models, it may be necessary to temporarily disconnect the oil level switch if it is stuck closed and not opening. To check the level switch, unplug the control board and verify that the MAGNETO KILL circuit on the control harness is not ground- ed. Refer to the Troubleshooting Chart.
3. CHECK FUEL SYSTEM If the engine cranks and has spark but does not start, the problem is likely fuel related. This can be confirmed by injecting a small amount of starting fluid into the air intake. If the engine fires and tries
to run, it is starving for fuel. Listen for the fuel pump running during cranking. Check for 12 volts at the FUEL PUMP pin on the control board during cranking. If there is no voltage, the control board is defective. The pres- sure and flow of the fuel pump (and fuel filter) can be checked by temporarily disconnecting the fuel line to the carburetor and jumpering the FUEL PUMP pin on the control plug to battery positive. Take adequate precautions when handling fuel. If pressure and flow are normal, reconnect fuel line. Note: If the generator has not been run for several months, the carburetor float may be stuck closed and /or the jets and needle valves may be gummed up by old fuel that has turned to varnish. These conditions interfere with normal fuel delivery. The automatic choke may be stuck closed or binding so that it does not open as the choke heater warms up. On Models BGM and NHM spec. B and later, make sure that the electronic governor goes to full throttle one second after cranking begins. Any of these conditions will prevent the engine from starting or running smoothly and must be corrected before proceed- ing.
4. CHECK IF ENGINE KEEPS RUNNING The most common complaint is that the engine starts but will not keep running when the START switch is released. This happens because the control board will not allow the engine to continue running if the generator is not producing voltage or if the oil pressure signal is not present. See CONDI- TIONS REQUIRED TO KEEP RUNNING on the Troubleshooting Chart for your model. If the engine will not keep running, do the following:
A1. Generator AC Output Check the generator AC output voltage as soon as the engine starts. Models showing “B1-B2 Volts” or “L1 AC Volts” under CONDITIONS REQUIRED TO KEEP RUNNING need this AC voltage to keep running. Read between the points shown on the Troubleshooting Chart. If the AC voltage readings are good, proceed to “B” below.
A2. Field Flash If there is no AC, check for 10-12 VDC at the FIELD FLASH pin of the control board dur- ing cranking. If the field flash voltage is not present, the control board is defective. If the field flash volt- age is present, the wiring or regulator may be defective. To eliminate the wiring, check continuity between the FIELD FLASH pin of the control board and pin 7 of the regulator. If the continuity is good, either the regulator or the field circuit (rotor and brushes) may be the problem.
A3 Field Circuit Check the field circuit by unplugging the regulator and measuring the resistance between pins 9 and 10 of the regulator’s mating plug. This reading should be 22 to 28 ohms. If this reading is too high, check the brushes and/or clean the slip rings (use the Slick Stick, or a similar tool). If this reading is too low, there may be a short in the rotor. Also, check the resistance from pins 9 and 10 to ground. This reading should be very high or infinity. If not, there is likely a ground in the rotor. If these reading are all
  3

A4 External Excitation To confirm that the regulator is defective, turn off the generator’s AC circuit breaker(s), reconnect the regulator and apply 12 volts through a diode to pin 9 of the regulator plug (see il- lustration) while attempting to start the engine. CAUTION: DO NOT attempt this without the diode. If you do, there will be fireworks! Remove the 12 volts within 1-2 seconds after the engine starts. If the genset now continues to run and produces normal AC voltage, the generator is OK and the regulator is defective.
If the genset does not continue to run but produces about 40% of normal AC voltage, again the generator is OK and the regulator is defective. If no AC voltage is produced, the generator may have a problem that is beyond the scope of this guide. Re-check all wiring for security and signs of damage. It may be necessary to take the unit to a qualified repair shop.
B. Check the oil pressure switch as soon as the engine starts. Models showing “LOP to GND” under CON- DITIONS REQUIRED TO KEEP RUNNING need the oil pressure switch to be closed to ground when running. If the voltage on the LOL/LOP SW pin of the control does not go to near zero, the switch is not closing. These switches sometimes stick open if the generator has not been used or exercised often enough. Multiple start/stop cycles and/or tapping on the oil pressure switch will sometimes fix it. It may be neces- sary to temporarily jumper the switch to ground to keep the engine running. This can be done at the switch or at the OIL LOL/LOP SW pin on the control board. Models showing “LOP Open” under CONDITIONS REQUIRED TO KEEP RUNNING have electronic governors and require the low oil pressure switch to be closed at starting but open during running. When the switch opens, the governor module places a ground on the oil pressure input of the control board (P1-5). It is OK to temporarily ground P1-5 on this model to keep the engine running. NOTE: See chart for oil pressure and oil level switch locations.
C. If there is AC voltage present on B1-B2 or L1 AC, as applicable, and the correct oil pressure/level signal is present at the OIL LOL/LOP SW input of the control board, and the engine will not keep running, the control board is defective.
1. After the engine has been running for a few minutes, the electric choke heater should begin to open the choke. The choke will take longer to open fully in cold weather. If the choke does not open, it is either stuck or the choke heater is not working. The choke mechanism can be freed up and maintained with “Mouse Milk”, a high tempera- ture penetrating lubricant.
2. If the engine surges or “hunts” (does not stay at a constant RPM), the cause is likely a gummed-up carburetor or an improperly adjusted governor. These conditions should be corrected. If your multi-meter has a “frequency” or a “Hz” range, you can check the RPM by measuring the frequency of the 120 VAC at the outlet. It should be approx- imately 62 Hz at no load and not go below 58 Hz at full load.
4

RV GENERATOR FAQs
The following FAQ’s apply primarily to Onan generators installed on many RV’s, but due to their general nature, may apply equally well to other makes. The information below is intended to help you get the best satisfaction from your RV genset and to enable you to find and correct some of the more common problems. Certain models are not covered because of their complexity and the need for specialized servicing tools. These include: Quiet Diesel Models HDKAJ, HDKAK and HDKAT; Microlite Model KY Spec. J and later; Camp Power Model KYD; Mobile Genset Models HG- JAB and HGJAC. Refer complex servicing to a qualified generator service facility.
Q. When the start switch is pressed in the coach or at the generator, nothing happens. What could be the problem?
A. The coach battery could be completely discharged or there could be a problem with a battery cable, the control board or the wiring. If the coach interior lights will not work, the problem is likely the coach battery. Check the battery and control fuse first. If the lights work, use the Troubleshooting Guide to isolate the problem.
Q. When the generator start switch is pressed, the starter makes a clicking sound but the engine does not crank. What is the problem?
A. Most likely, the coach battery is almost completely discharged and needs to be charged or replaced. There could also be a poor connection or a defective battery cable or starter solenoid. If these causes can be eliminated, then the starter itself may need service.
Q. Why does my generator crank over normally but not start?
A. The problem is either fuel or ignition related. If the engine tries to run when a small amount of starting fluid is sprayed into the air intake, it is a fuel problem. The ignition can be checked by removing and grounding a spark plug. Refer to the “Getting the Engine Running” section of the Troubleshooting Guide to isolate the problem.
Q. Why does my generator start and then shut down as soon as the start switch is released?
A. Most models require both oil pressure and AC voltage from the generator to keep running. A lack of AC voltage can be caused by a variety of problems involving the control board, regulator, generator and wiring. A stuck oil pressure switch can also cause this symptom. The interaction between the various components of the system can be confusing during troubleshooting. Use the Troubleshooting Guide to isolate the problem.
Q. The start switch works at the generator but not from inside of the coach. What is the problem?
A. The remote start/stop control is not connected to the control board. Make sure the remote connector is plugged in to
the control at the generator. Check remote switch and wiring.
Q. The start switch works from inside of the coach but not at the generator. What is the problem?
A. The start switch on the control board or control panel is defective. Replace the switch or control board, as appli- cable.
Q. Why does my generator run rough and/or smoke, even after it is warmed up?
A. This can be caused by the electric automatic choke not opening (choke stuck or choke heater not working), an improperly adjusted carburetor (too rich), or a sticking carburetor float that allows excess fuel to enter the carburetor bowl. Rough running can also be caused by fouled spark plugs.
5

Q. Why does the generator RPM surge up and down and not stay at a constant speed?
A. Surging is caused by a gummed-up or improperly adjusted carburetor or an improperly adjusted governor.
Q. My generator starts OK, runs for a while and then shuts down. Sometimes, it can be re-started after cooling for a few minutes. What causes this?
A. The most likely cause is fuel starvation. This can be caused by low fuel level (not getting gas), vapor lock (too hot, gas is boiling), fuel contamination (water or dirt in fuel and/or filter) or a faulty fuel pump (insufficient fuel pressure). Models equipped with low oil level (LOL) switches will shut down the engine on low oil level.
Q. What can I do to prevent fuel from deteriorating and causing problems during periods of non use?
A. Regular exercise is a big help, but a fuel stabilizer such as “STA-BIL” should be added to the fuel at the start of the storage period. Follow the manufacturer’s recommendations and remember to run the generator long enough to get the treated fuel into the system.
Q. My generator was running great at the end of last season but now it has problems. What could be the cause or causes?
A. The generator was likely not exercised often enough or at all during the last period of non-use. A stabilizing addi- tive may not have been added to the fuel (see Q & A above). There could be latent corrosion damage from road chemi- cals or wiring damage from rodents. The problem could be simply a stuck oil pressure switch. The problems expe- rienced could be for a variety of causes. Generators need regular use or exercise in order to remain trouble-free. See next Q&A below and also “Troubleshooting”.
Q. How often should an RV generator be exercised and what is the procedure?
A. All RV generators should be exercised at least once per month during periods of non-use. Make sure external AC power is disconnected from the coach and the coach battery is charged. Start the generator and wait a couple of min- utes for warm-up, longer in very cold weather. Load the generator by plugging in a ceramic-type portable electric heater (approx. 1KW). When the outside temperature is above 65F, use the roof air conditioner to load the generator. Allow the generator to run under load for 20-25 minutes. Remove the load and run for another 2-3 minutes as a cool down period, then shut down.
Q. The voltage at the AC outlet is too high (above 125 VAC at no load) on start up, or gradually climbs after the gen- erator has been running for a while. What causes this?
A. If the voltage is somewhat high or climbs, the regulator is defective and needs to be replaced. If the voltage imme- diately goes to 160 VAC on start-up, the problem is either the regulator or a loose connection at pin 2 of the regulator. Check connections before replacing the regulator.
Q. The voltage at the AC outlet is too low (below 112 VAC at no load) or goes down more than a few volts when a load is added. What causes this?
A. First, make sure that the generator is running at rated speed. This can be done with a multi-meter that has a “fre- quency” or a “Hz” range. Make sure the slip rings are clean. Check the connections between pins 4 and 5
(or pins 1 and 5 on Microlite 2.8KW) on the regulator, as this can cause an output voltage of 55-60 VAC, even with a good regulator. When these causes have been eliminated, the regulator is likely defective.
6

Q. With the generator running, there is no 120 VAC at any of the outlets. What is the problem?
A. The AC circuit breaker(s) at the generator may be turned off or tripped. Check the breaker(s) first. Make sure that there is 120 VAC at the generator (L1-L2 on the terminal block or pins 2-3 on the regulator plug). If the circuit breaker is on, there is 120 VAC at the generator and there is still no voltage at the outlets, the problem could be a faulty transfer relay. This device is located in the coach and is not part of the generator. Its job is to switch the AC load from the com- mercial power to the generator when it is running.
Q. What are slip rings, where are they located and what is their function?
A. Slip rings are two flat metal rings located side by side on the rear of the rotor (end away from the engine) that pro- vide a means of contact for the brushes. The brushes run against the slip rings and carry the current (field current) required for magnetizing the rotor.
Q. Why do the generator’s slip rings require cleaning periodically?
A. During periods of storage and a lack of regular exercise, RV generator slip rings can become corroded, particularly in areas near salt water. Even with regular running, a layer of oxide and brush residue can build up on the rings, in- creasing their electrical resistance. Proper cleaning (such as with the Slick Stick Slip Ring Cleaning Tool, available from Flight Systems) restores the running surface to like-new condition. This results in cooler running as well as ex- tended brush and regulator life. Dirty slip rings can cause overheating and premature regulator failure.
Q. How can I determine if the slip rings need to be cleaned?
A. A quick visual inspection can be done by looking through the cooling slots at the rear of the generator with a bright light. The slip rings should appear as shiny clean metal. You can also unplug the regulator and measure the resistance between pins 9 and 10 of the plug that was connected to the regulator. If this reading is greater than 28 ohms, cleaning is needed.
Q. Is there a place where I can easily check for the proper voltages when the generator is running?
A. Yes. The 120 VAC and/or 60 Hz frequency can be checked between pins 2 and 3 of the regulator or at any outlet, and should be between 117 and 126 VAC at no load. The field voltage can be checked between pins 9 and 10 of the regulator and should be 35-40 volts at no load and rise to about 60 volts at full load.
7

 8

 9

   10

  11

 300-2784/2943 (FLIGHT SYSTEMS REPLACEMENT)
 12

  13

  14

  15

 16
 

Link to comment
Share on other sites

Join the conversation

You can post now and register later. If you have an account, sign in now to post with your account.

Guest
Reply to this topic...

×   Pasted as rich text.   Paste as plain text instead

  Only 75 emoji are allowed.

×   Your link has been automatically embedded.   Display as a link instead

×   Your previous content has been restored.   Clear editor

×   You cannot paste images directly. Upload or insert images from URL.

Loading...
×
×
  • Create New...