12 hours ago, GlennWest said:

But what if I disconnect the neutral to ground at the pole and reconnect at camper? 

When I last practiced Power Distribution Engineering THAT WAS NEVER DONE but I'm not up on the latest codes so NO warranty. AFTER the ONE and ONLY permissible NG Bond (at the first disconnect) for 120/240 Volt Single Phase Three Wire service you would carry FOUR WIRES.........Two UNgrounDED  Conductors L1 & L2,,,,,,,,,,,,One GrounDED Conductor (aka Neutral),,,, One Safety Equipment GroundING Conductor.   

 Then any later sub panels be it an RV or whatever, The Neutral Buss and Equipment GroundING Buss are kept separate insulated and isolated from each other. Its not that hard and requires ONLY one more wire and unless the code has changed ??? thats how its done but do as you please is fine with me its YOUR choice not ours

NOTE not being there and not knowing what's at the pole (is it first means of disconnect??) DO NOT TAKE THIS AS THE LATEST,,, consult the NEC and any local governing authority if any is applicable in your area  DO NOT TAKE MY WORD FOR IT this is ONLY my best recollection and how it was years ago

 John T

 

 

 

 

Link to comment
Share on other sites

  • Replies 85
  • Created
  • Last Reply

Top Posters In This Topic

Glenn my house has 3 wires coming off the transformer to the meter, 2 110 and a neutral, then a switch. The neutral and the ground are common at the meter. 3 wires going 600 feet, 0000 aluminium then a switch then to the panel the neutral and a ground are isolated at the panel. It's been this way for 35 years and I don't know if it's correct but I bought everything from the power company when I installed it. The only conduit used was at the pole into the ground. use a sliding conection, I didn't and that's a mistake at least in freezing country, and were it comes out of the ground and into the house and over a ledge that is under the driveway. 

Link to comment
Share on other sites

See that is what I was thinking of doing. So I am getting conflicting info. I just came from my property looking at it. My meter base is 3 in and out. My 200 amp box is common ground and neutral. It does have 2 lugs on the common ground/neutral. A bare copper about #8 goes to a 5/8" copper rod in ground. So being it is common a #4/0 neutral is all that is needed but is it legal? I can much cheaper make a ground at camper site. My home would have proper grounding and panel at post have proper grounding. Just the buried wire would have no separate ground.  

2003 Teton Grand Freedom towed with 2006 Freightliner Century 120 across the beautiful USA welding pipe.https://photos.app.goo.gl/O32ZjgzSzgK7LAyt1

Link to comment
Share on other sites

16 minutes ago, GlennWest said:

My 200 amp box is common ground and neutral. It does have 2 lugs on the common ground/neutral. A bare copper about #8 goes to a 5/8" copper rod in ground. So being it is common a #4/0 neutral is all that is needed but is it legal? I can much cheaper make a ground at camper site. My home would have proper grounding and panel at post have proper grounding. Just the buried wire would have no separate ground. 

1) "My 200 amp box is common ground and neutral"

   Thats what I would expect and is code proper when I last practiced, that's your Neutral Ground Bond creation........of which there should BE ONLY ONE  alls well so far

2) "A  bare copper about #8 goes to a 5/8" copper rod in ground"

   That's connection of the Neutral to a "Made Grounding Electrode" (Grounding NOT Bonding), fine and expected other then I uses a soft bare copper # 4 conductor NOT No 8.

3) "So being it is common a #4/0 neutral is all that is needed but is it legal?"  WHATS LEGAL IS RUNNING A SEPARATE GROUNDED CONDUCTOR (aka Neutral) PLUS a separate Equipment GroundiNG Conductor to any downstream sub panels IE NOTTTTTTTTTTTTT NEUTRAL ONLY. For 120/240 Volt Single Phase Three Wire from a main to a sub (or RV panel) you need FOUR wires,,,,,,,,Two Hots, Neutral, Ground and the sub like RV panels have separate insulated and isolated Neutral and Ground Busses NOT a single common buss  

 Theres no other way of saying this, so wire it anyway you please and sure it can still work. I am ONLY describing it the way the NEC (as I best recall no warranty) called for it to be done when I last practiced Power Distribution Engineering

PS I don't think you understand the difference between Grounding and Bonding but don't feel bad many non electrician non electrical engineers don't either lol

Good luck with it take care be safe and best wishes

John T

 

Link to comment
Share on other sites

Actually John, The trailer that was previously in there they just cut the lines. They skinned the wire far back to go in both lugs. So on common/ground to trailer. Just 3 wires. He also has a 60 amp breaker in there running an underground line to removed trailer. Don't know what that used for.  Concerning the wiring, the neutral and ground is together in the box. They just supply two lugs. So you saying run two lines off of there and call one ground and one neutral. They are both the same in reality. 

Edited by GlennWest

2003 Teton Grand Freedom towed with 2006 Freightliner Century 120 across the beautiful USA welding pipe.https://photos.app.goo.gl/O32ZjgzSzgK7LAyt1

Link to comment
Share on other sites

A quick call to the electrical inspector will provide what is acceptable in your area.  Here I have called them and received answers without a permit or even giving them my name.  At least then you will know what code requires.  If you decide to skirt the code no one on this forum can help if it becomes an issue.

Randy

2001 Volvo VNL 42 Cummins ISX Autoshift

Link to comment
Share on other sites

7 minutes ago, Randyretired said:

A quick call to the electrical inspector will provide what is acceptable in your area.  Here I have called them and received answers without a permit or even giving them my name.  At least then you will know what code requires.  If you decide to skirt the code no one on this forum can help if it becomes an issue.

I will do whatever is needed. Don't understand why it is needed. 

2003 Teton Grand Freedom towed with 2006 Freightliner Century 120 across the beautiful USA welding pipe.https://photos.app.goo.gl/O32ZjgzSzgK7LAyt1

Link to comment
Share on other sites

1 hour ago, GlennWest said:

I will do whatever is needed. Don't understand why it is needed. 

Heres why:

 The Safety Equipment GroundING Conductor is a dedicated low resistance return path designed to carry FAULT CURRENT ONLY.  Its designed to NEVER carry normal current, that's the job of the Neutral GrounDED conductor described below

 The GrounDED Conductor aka Neutral is designed to carry all normal return current.

 The Neutral Conductor is insulated as its a HOT live current carrier UNLIKE the often bare Equipment GroundING Conductor which can be attached to the outer metallic conductive case/frame of a tool or appliance which you touch.

YES once the Neutral Ground BOND is established (like a common Neutral Ground Buss Bar in a main panel) you carry two wires (Neutral and Ground) from there THAT SAME PLACE  to a downstream Sub or RV Panel which has separate insulated and isolated Neutral and Ground Busses. HOWEVER the ground ONLY carries fault current while the Neutral carries normal return current.

Best I can do Glenn, DO NOT feel bad if you dont understand it most non electricians non engineers dont either lol

 

AGAIN wire as you please its NOT my job to tell you how. Consult local trained professional electricians and engineers NOTTTTTTTTTTT me Im rusty on this even if it constituted much of my lifes work and training......

 

John T   BSEE,JD  Longgggggggg retired

Link to comment
Share on other sites

Join the conversation

You can post now and register later. If you have an account, sign in now to post with your account.

Guest
Reply to this topic...

×   Pasted as rich text.   Paste as plain text instead

  Only 75 emoji are allowed.

×   Your link has been automatically embedded.   Display as a link instead

×   Your previous content has been restored.   Clear editor

×   You cannot paste images directly. Upload or insert images from URL.

Loading...

RVers Online University

mywaggle.com

campgroundviews.com

RV Destinations

Find out more or sign up for Escapees RV'ers Bootcamp.

Advertise your product or service here.

The Rvers- Now Streaming

RVTravel.com Logo



×
×
  • Create New...