Any input on voltage drop and how I might better prevent it is welcome. Thank you!
Roll Me Away
Posted 13 April 2012 - 10:16 AM
Posted 13 April 2012 - 10:26 AM
Posted 13 April 2012 - 11:01 AM
Posted 13 April 2012 - 11:17 AM
Edited by Mark & Dale Bruss, 13 April 2012 - 02:20 PM.
Please Emails only
Mark & Dale
Red Rover - 2000 Volvo 770, Tige - 2006 40' Travel Supreme
Sparky II - 2012 Chevy Equinox, Living on the Road since 2006
Useful Truck, Trailer, and Full-timing Info at
www.dmbruss.com
Posted 13 April 2012 - 11:21 AM
Edited by AFChap, 13 April 2012 - 11:23 AM.
Posted 13 April 2012 - 11:57 AM
Posted 13 April 2012 - 12:11 PM
What product do you have from Surge Guard? Is it this 34730, which will protect you and your RV from low or high voltages by simply turning off all power until it recovers, or do you have one of the less expensive surge protectors which do nothing more that stop large power surges? While both items come from TRC and sell under the brand name Surge Guard, they are very different things and have completely different characteristics.I've a class C RV and have a SurgeGuard 30 amp surge protector, however, recently experienced problems that the techs said came from low voltage.

Posted 13 April 2012 - 12:54 PM
Rif,I always use the EMS when I first plug into the power pole. It will check for everything, and as long as the power is OK, that is all I use. However, if I subsequently encounter a low voltage situation, which often does not occur until hours or days later, I will install the Autoformer. Since I have already satisfied myself that things are fine except for the low voltage, and since the Autoformer will also provide me with spike and surge protection while boosting the voltage, I turn off the EMS. While I would prefer to leave both on, the EMS is much faster reacting than the Autoformer, and shuts off the power before the Autoformer can boost the voltage. The time delay is milliseconds and does not last long enough to harm my appliances, but it will be very disruptive as it cuts off the power temporarily. Shutting off the EMS in this situation prevents this from happening.
I am a strong proponent of EMS systems, and they work well to prevent damage to my rig and appliances. But I have also become a fan of Autoformers since they allow me to actually do something about the common issue of low voltage.
Posted 13 April 2012 - 01:22 PM
Rif,
We put our Autoformer upstream from the EMS so it boosts the power before the EMS. We leave both online and they work well together. Our EMS has never tripped for low voltage with the Autoformer inline.
Walkerl
Posted 13 April 2012 - 01:44 PM
Posted 13 April 2012 - 02:18 PM
Posted 13 April 2012 - 03:26 PM
surge protectors
What product do you have from Surge Guard? Is it this 34730, which will protect you and your RV from low or high voltages by simply turning off all power until it recovers, or do you have one of the less expensive surge protectors which do nothing more that stop large power surges? While both items come from TRC and sell under the brand name Surge Guard, they are very different things and have completely different characteristics.
Whether you get a line protection device from Surge Guard or one from Progressive, either one will protect your equipment from too high or too low of power line voltages as well as a host of other things, but neither of them will solve the problem, they simply turn off the power when it sags too low for safety or if it should rise too high. If you want something that will allow you to continue to operate your electrical loads safely, even when the park power voltage sags to dangerous levels, then what you need to get is an Autoformer by Hughes. This product will in fact boost poor voltage to where you can safely continue to use your air conditioner and other electrical equipment. It has somewhat less monitoring capability than either of the other two, but it probably is what you need where you are, unless you are willing to move.
Electrical power requirements are not a simple thing and to really understand the problems takes more than a little electrical training, but you can protect yourself and your equipment without a great deal of difficulty, but not cheaply. Based upon your note that you have ordered the Progressive EMS it is important that you realize that it will not boost your power line voltage at all, but simply removes power when the voltage sags to dangerous levels. If this happens a great deal you will probably not be very happy as you will be without any electrical power for as long as that voltage stays below 108V. What you ordered is protection, but not a power boost.
Posted 13 April 2012 - 03:47 PM
Kirk, thanks for the information(thanks to others as well). I wish I understood how the autoformer works. Does it produce more voltage? From where if voltage is low? I will definitely check it out and see if I can find a place to put it in my rather limited space (27 feet is not a lot of room in the little cubbyholes around the area of electrical input). The SurgeGuard is the big one, 30 amp, and it does have indicators of line problems, but nothing definitive. It has a delay mechanism when it shuts down and comes on again. Nothing in the packet said anything about voltage, just that it protects from surges. I called the Progressive because I've read a lot of good info on it, the forum member guided me to look into it, and the Progressive fellow called me right back and had a lot of apparently good information on it. Evidently it will block surges and also shuts off voltage over 132v and under 104v, thus hopefully saving equipment. He suggested the exterior portable as it does the same thing as the hardwired and my space is limited. The autoformer appears to be good to use with the {EMS?) if I'm reading the posts here correctly.
Thing is, in this universe of information not all of it is correct and much is in gray areas, partially correct and partially incorrect, so one has to process it, ask questions, and try to make correct choices. I have looked to members of the forum, those who are experienced and knowledgeable for advice and ideas. Maybe there's a forum where people share the electrical adequacy of the parks they've enjoyed most and safest. Anyway, I will read all posts on this subject and the autoformer and appreciate whatever I learn.
Roll Me Away
The hardwire EMS unit is quite compact and can be installed in a very small space. It has the advantage of being theft proof.
Posted 13 April 2012 - 05:09 PM
I wish I understood how the autoformer works. Does it produce more voltage? From where if voltage is low?
Posted 13 April 2012 - 06:15 PM
As Stanley said, it uses a device that is called an autotransformer. Electrical power is all about the relationship between volts(which is the driving force) and amps(which is the measure of volume as gallons of water). When you multiply the two you get watts, which is the amount of work done.I wish I understood how the autoformer works. Does it produce more voltage? From where if voltage is low?
If you have not yet bought the progressive, you need to check to see what model of Surge Guard you have. I have used one for 10 years and I do know that if you have the model 34730, it is a 30A model with complete line monitor capability and you do not need to buy more. If you have a model 34750 it is the same but a 50A model. Those are both portables that attach to the power pedestal, if permanently installed the model numbers would be 34520 for 30A and 34560 for the 50A version. It you have a simple surge suppressor from Surge Guard, then the model is 44740. You need to first determine what you have before you spend any more money!The SurgeGuard is the big one, 30 amp, and it does have indicators of line problems, but nothing definitive. It has a delay mechanism when it shuts down and comes on again. Nothing in the packet said anything about voltage, just that it protects from surges.
Progressive is a competing company to TRC who is the parent of the Surge Guard line and they do not make some of the things that TRC does. You can get a voltage boost system from TRC which will do the same things as you get with the Autoformer.I called the Progressive because I've read a lot of good info on it, the forum member guided me to look into it, and the Progressive fellow called me right back and had a lot of apparently good information on it. Evidently it will block surges and also shuts off voltage over 132v and under 104v, thus hopefully saving equipment. He suggested the exterior portable as it does the same thing as the hardwired and my space is limited. The autoformer appears to be good to use with the {EMS?) if I'm reading the posts here correctly.
Edited by Kirk, 13 April 2012 - 06:21 PM.

Posted 13 April 2012 - 07:38 PM
The autoformer is short for automatic transformer. It increases the voltage it puts out by drawing a bit more current from the shore power and converting that into more volts for resistive loads. For motor loads it will often put the motor into a more efficient voltage range reducing the current it needs so the result is less current pulled from the shore power.
Posted 13 April 2012 - 08:02 PM
Actually autoformer means self transformer. It is so named because the single winding is both primary and secondary. See an explanation here Autoformer explanation

Posted 13 April 2012 - 10:00 PM
Posted 14 April 2012 - 06:52 AM
As Stanley said, it uses a device that is called an autotransformer. Electrical power is all about the relationship between volts(which is the driving force) and amps(which is the measure of volume as gallons of water). When you multiply the two you get watts, which is the amount of work done.
A transformer changes voltage either up or down, depending upon the design. If that transformer takes 100V and boosts it up to 120V, an increase of 20%, it does so by drawing more amps of current into the primary side by an increase of current of 20%. If the output was supplying 10A at 100V without the step up from the transformer, then to boost that power to 10A at 120V the primary side will require a 20% increase, or 12A into it to send out the same 10A as before but at the higher voltage. The design of an autotransformer is such that when the input is at the same voltage that it is designed to supply, it simply passes the voltage and current through, with no effect at all, but if the voltage into it begins to sag it will send out the designed voltage, but in doing so it requires more amps to do this. One can get very technical in the explanation of what actually happens and have all kinds of very technical discussions, but in simple layman's terms, it is that simple. If you priced the Autoformer, you have probably figured out that this has a lot of design and hardware involved, but this is basically what happens.
If you have not yet bought the progressive, you need to check to see what model of Surge Guard you have. I have used one for 10 years and I do know that if you have the model 34730, it is a 30A model with complete line monitor capability and you do not need to buy more. If you have a model 34750 it is the same but a 50A model. Those are both portables that attach to the power pedestal, if permanently installed the model numbers would be 34520 for 30A and 34560 for the 50A version. It you have a simple surge suppressor from Surge Guard, then the model is 44740. You need to first determine what you have before you spend any more money!
Progressive is a competing company to TRC who is the parent of the Surge Guard line and they do not make some of the things that TRC does. You can get a voltage boost system from TRC which will do the same things as you get with the Autoformer.
I strongly suggest that we need to determine exactly what you have now, before you buy something else. You may spend a lot more money that is needed. If you click on the links that I have provided, each one will show you a picture of the device mentioned.
Edited by Roll Me Away, 14 April 2012 - 06:55 AM.
Posted 14 April 2012 - 07:03 AM
First off, the problem with low voltage usually comes from the park wiring.
And don't blame the 50 amp motorhomes. Quite often whenever we ran into low voltage it was on a 30 amp service.
One of the things that can cause intermittent low voltage is a bad neutral circuit. It is more obvious on a 50 amp service because you will see one leg drop and the other leg rises. With 30 amp services, it is common for two adjacent sites to be like a 50 amp service, not in amperage but in the fact that with a poor neutral, one site will drop while the other will rise.
What happens is that the current draw of devices like an AC unit will drag the neutral toward the leg with the current draw. That is indicated by a lower voltage reading. In the meantime, the other leg is farter away from the neutral electrically with a higher voltage reading.
A analog voltmeter is fine for this checking, in fact may even be better because you can see the needle swing as voltage changes.
This problem is one of the best for proving the need of an EMS. People who only meter power pole receptacles before plugging in will never see this condition as it exists only with a load. The EMS monitors conditions all the time, far safer.